    Quote Originally Posted by 53 View Post
    Suckerforhorses -can the grounding wire drape over (and touch) the edge of the rubbermaid tank?
    Yes, no problems with that.

    Our tank is up against a building, whose face is part of the "paddock". I have the tank flush to the wall, and because its a 150 gallon tank, they don't bother reaching to the back of it/to the wall to where the outlet is. The outlet is an outdoor GFCI type outlet.

    Directly behind the tank, is the ground rod so its not out where the horses can of course cause damage to themselves with it, as horses will always do!

    Wire clamped to ground rod, then, up over the side of the tank (I bent it to "squeeze" the side of the tank so it doesn't move around) and then the end right into the water, and is long enough so the wire goes to the bottom of the tank (so I don't risk the water level getting lower than the wire).

    I have the wire going in more to the side, just so the wire isn't touching the heating element itself. I'm not sure that it would matter, but thats the way I chose to keep them separate.
    "If you think nobody cares about you, try missing a couple payments..."



  2. #42
    Join Date
    Feb. 1, 2012
    Location
    Vermont
    Posts
    5,394

    Default

    I'm not sure the "type" of wire that we used, that's not my department but the SO's but the wire itself is about the diameter of a pencil at least. So, it's not like skinny electric fence wire, but thicker.

    I'm not sure if it matters, someone more knowledgable about grounding could probably answer that. I think the diameter has to do with the wire's capability of "sucking up the juice" out of the water.

    I'm not very techical about the terms...
    "If you think nobody cares about you, try missing a couple payments..."



  3. #43
    Join Date
    Nov. 1, 2005
    Location
    The Prairie
    Posts
    5,457

    Default

    Quote Originally Posted by OTTBcooper View Post
    Is your water staying warm just by being inside the insulated box, and you are not using a heater? If so - any chance you'd be willing to share pictures?!
    No, I am still using a heater. I am on the Canadian prairie, right now it is -28 Celsius outside (warmest day all week as a matter of fact.....) If I did not use a heater the water would be a big chunk of ice in about an hour. My hope with the cover was to keep the heater from working too hard and it has worked really well. I will try to take some pics this weekend, when I am outside in the daylight!
    I love cooking with wine. Sometimes I even put it in the food.



  4. #44
    Join Date
    Nov. 1, 2005
    Location
    The Prairie
    Posts
    5,457

    Default

    Quote Originally Posted by SuckerForHorses View Post
    Yes, no problems with that.

    Our tank is up against a building, whose face is part of the "paddock". I have the tank flush to the wall, and because its a 150 gallon tank, they don't bother reaching to the back of it/to the wall to where the outlet is. The outlet is an outdoor GFCI type outlet.

    Directly behind the tank, is the ground rod so its not out where the horses can of course cause damage to themselves with it, as horses will always do!

    Wire clamped to ground rod, then, up over the side of the tank (I bent it to "squeeze" the side of the tank so it doesn't move around) and then the end right into the water, and is long enough so the wire goes to the bottom of the tank (so I don't risk the water level getting lower than the wire).

    I have the wire going in more to the side, just so the wire isn't touching the heating element itself. I'm not sure that it would matter, but thats the way I chose to keep them separate.
    I have never grounded it like this and so far never had a problem but I will definitely remember this if I ever do. I'm sure my luck will run out eventually. I actually have a ground rod for my electric fence fairly close to my water tank, I think I could connect a wire to that ground rod. Thanks for the info.
    I love cooking with wine. Sometimes I even put it in the food.



  5. #45
    Join Date
    Feb. 1, 2012
    Location
    Vermont
    Posts
    5,394

    Default

    I'm not so sure they should share a ground rod...what if your fencer puts juice back into the ground rod, which travels up the wire into your water??? I think you should use its own ground rod & wire for the water tub.
    "If you think nobody cares about you, try missing a couple payments..."



  6. #46
    Join Date
    Nov. 1, 2005
    Location
    The Prairie
    Posts
    5,457

    Default

    Hmm.
    Doesn't the electricity "want" to go into the ground? I will ask my fence builder...he knows all!
    I love cooking with wine. Sometimes I even put it in the food.



  7. #47
    Join Date
    Mar. 30, 2004
    Location
    Lexington, KY
    Posts
    2,972

    Default

    My DH just ran a short extension cord from the barn to the tank and stuck his diesel engine block heater onto the outside of the metal tank that's wedged up against the fence corner, so no chewers hopefully. We'll see if that works.
    send some of their smart literate deer who can read road signs up here since ours are just run of the mill dumb ones who get splatted all over creation because they won't stay in the woods



  8. #48
    Join Date
    Feb. 1, 2012
    Location
    Vermont
    Posts
    5,394

    Default

    Quote Originally Posted by Mozart View Post
    Hmm.
    Doesn't the electricity "want" to go into the ground? I will ask my fence builder...he knows all!
    Yes, but if you have a wire from your tank water attached to the ground rod that is also attached to your fencer ground, you are creating a path for any voltage from your fencer to just hit the rod, and then travel up the wire that you also have going into your tank.
    "If you think nobody cares about you, try missing a couple payments..."



  9. #49
    Join Date
    Feb. 1, 2012
    Location
    Vermont
    Posts
    5,394

    Default

    And if that electricity travels into your water, you're going to have horses getting shocked from the fencer electricity
    "If you think nobody cares about you, try missing a couple payments..."



  10. #50
    Join Date
    Sep. 11, 2011
    Location
    Charlottesville, VA
    Posts
    269

    Default

    Quote Originally Posted by SuckerForHorses View Post
    No, your horse isn't drinking from it because there is likely stray voltage in the water, and she's getting shocked. See my post above to explain how to fix this.
    Ahhh thank you! I switched to the 16g heated tub and same thing, only now she goes for the water and snaps back like she is actually being shocked. Im going to ground it tomorrow like you suggested. What size wire would you recommend?
    "No hour of life is wasted that is spent in the saddle" - Winston Churchill

    Check out Central Virginia Horse Rescue



  11. #51
    Join Date
    Sep. 24, 2004
    Location
    Piedmont Triad, North Carolina
    Posts
    2,395

    Default

    Quote Originally Posted by OTTBcooper View Post
    Ahhh thank you! I switched to the 16g heated tub and same thing, only now she goes for the water and snaps back like she is actually being shocked. Im going to ground it tomorrow like you suggested. What size wire would you recommend?
    Are you using grounded extension cords? Do all of the cords have original factory connectors (both male or female ) Does the heater cord have a 3 element plug?

    The reason for these questions is all electrical circuits have a hot leg , neutral and ground. If any of these gets switched, the ground wire stops being ground and becomes a path for electric shock.

    If the answer to any of the ? is no ... this could be a possibility. Outlet could also be wired incorrectly.



  12. #52
    Join Date
    Sep. 11, 2011
    Location
    Charlottesville, VA
    Posts
    269

    Default

    Quote Originally Posted by hosspuller View Post
    Are you using grounded extension cords? Do all of the cords have original factory connectors (both male or female ) Does the heater cord have a 3 element plug?

    The reason for these questions is all electrical circuits have a hot leg , neutral and ground. If any of these gets switched, the ground wire stops being ground and becomes a path for electric shock.

    If the answer to any of the ? is no ... this could be a possibility. Outlet could also be wired incorrectly.
    Yes to grounded extension cords, all have original factory connectors, and all have 3-prong plugs. I am thinking that the darn outlet was wired incorrectly (we've come across a few others that were done incorrectly since we purchased the house 6 months ago). Is my best bet using the grounded rod and grounding wire in the trough or trying to fix the outlet?

    Also.... if I have two tubs, can I run two wires from the grounding rod, one to each water trough or will that defeat the purpose?
    "No hour of life is wasted that is spent in the saddle" - Winston Churchill

    Check out Central Virginia Horse Rescue



  13. #53
    Join Date
    Feb. 1, 2012
    Location
    Vermont
    Posts
    5,394

    Default

    Quote Originally Posted by OTTBcooper View Post
    Is my best bet using the grounded rod and grounding wire in the trough or trying to fix the outlet?

    Also.... if I have two tubs, can I run two wires from the grounding rod, one to each water trough or will that defeat the purpose?
    I would have the outlet checked by an electrician and fixed if possible, and use the grounding rod.

    I believe 1 rod per tank (not sharing them) would be the best way to go. As I mentioned above, if you have both wires connected to one rod, I think what will happen if you have say only 1 tank emitting stray voltage to the ground rod, is that the voltage can travel back out the other wire and into the water of your second tank. I'm not an electrician, but it seems like that would be a logical possible thing that could happen.
    "If you think nobody cares about you, try missing a couple payments..."



  14. #54
    Join Date
    Sep. 2, 2005
    Location
    Upstate NY
    Posts
    12,772

    Default

    My opinion is while you have an electrician out there to fix your not grounded outlets ask them about the need for the grounding rod at the tank, etc.



  15. #55
    Join Date
    Sep. 11, 2011
    Location
    Charlottesville, VA
    Posts
    269

    Default

    SuckerForHorses and trubandloki - thanks to both! Will have electrician out and go from there.... might not even need the heaters by the time we get it fixed, hah
    "No hour of life is wasted that is spent in the saddle" - Winston Churchill

    Check out Central Virginia Horse Rescue



  16. #56
    Join Date
    Apr. 6, 2009
    Location
    Mowrystown, OH
    Posts
    6

    Default

    We are having trouble with ours, too. One of my horses will drink, the other two act like they are getting shocked. We had everything checked out by an "electrician", but he never suggested grounding the trough. One of our friends is an industrial electrician, and he told us about grounding the trough.



  17. #57
    Join Date
    Sep. 11, 2011
    Location
    Charlottesville, VA
    Posts
    269

    Default

    Quote Originally Posted by balakai View Post
    We are having trouble with ours, too. One of my horses will drink, the other two act like they are getting shocked. We had everything checked out by an "electrician", but he never suggested grounding the trough. One of our friends is an industrial electrician, and he told us about grounding the trough.
    Ditto. Had our outlet and then all downstairs outlets checked by an electrician. He even checked the extension cord, and the connection of the extension cord to the house and to the bucket. Nothing wrong with anything but horses still being shocked. I will probably have to do the grounding rod idea :-/ what a pain
    "No hour of life is wasted that is spent in the saddle" - Winston Churchill

    Check out Central Virginia Horse Rescue



  18. #58
    Join Date
    Feb. 1, 2012
    Location
    Vermont
    Posts
    5,394

    Default

    Quote Originally Posted by OTTBcooper View Post
    Ditto. Had our outlet and then all downstairs outlets checked by an electrician. He even checked the extension cord, and the connection of the extension cord to the house and to the bucket. Nothing wrong with anything but horses still being shocked. I will probably have to do the grounding rod idea :-/ what a pain
    We also went through a bunch of electrical troubleshooting, and out electrician didn't mention anything about grounding my tank/water. I found the grounding instructions...wait for it....on the instructions that came with the heater...
    "If you think nobody cares about you, try missing a couple payments..."



  19. #59
    Join Date
    Sep. 11, 2011
    Location
    Charlottesville, VA
    Posts
    269

    Default

    Quote Originally Posted by SuckerForHorses View Post
    We also went through a bunch of electrical troubleshooting, and out electrician didn't mention anything about grounding my tank/water. I found the grounding instructions...wait for it....on the instructions that came with the heater...
    Hah, now there's an idea! I don't think my heated tubs came with instructions but I'm definitely going to look it up online.
    "No hour of life is wasted that is spent in the saddle" - Winston Churchill

    Check out Central Virginia Horse Rescue



Similar Threads

  1. Water Trough Heaters
    By cripplecreekfrm in forum Around The Farm
    Replies: 4
    Last Post: Nov. 15, 2010, 08:58 PM
  2. Propane stock tank heaters
    By f4leggin in forum Around The Farm
    Replies: 1
    Last Post: Dec. 7, 2009, 01:46 PM
  3. Tank heaters for the smaller tank?
    By greysandbays in forum Horse Care
    Replies: 0
    Last Post: Oct. 9, 2009, 02:35 PM
  4. What tank heaters do to your electric bill!
    By SCF01 in forum Around The Farm
    Replies: 19
    Last Post: Jan. 8, 2009, 03:33 PM
  5. math: stock tank heaters, tack room heaters and KwHs
    By pintopiaffe in forum Off Course
    Replies: 17
    Last Post: Nov. 25, 2008, 02:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •